AmarnepalNepal Data
Infrastructure & transport

New Electricity Connection in Nepal: NEA Meter Application Guide

To get a new NEA electricity connection in Nepal, submit the new customer application form at your nearest Nepal Electricity Authority distribution centre with your citizenship certificate, land ownership certificate (lalpurja) or rental agreement, building approval and ward recommendation, choose an ampere band (5–60 A single-phase or three-phase), pay the service charge and deposit, and pass the household wiring inspection. NEA has publicly committed to installing single-phase meters within about seven days of completed paperwork; three-phase applications can also be filed online at crm.nea.org.np.

UtilityNepal Electricity Authority (NEA), established Bhadra 1, 2042 BS (16 August 1985 AD)
Where to applyNearest NEA distribution centre (bitaran kendra); three-phase also online at crm.nea.org.np
Core documentsCitizenship certificate, lalpurja or rental agreement, building/map approval, ward recommendation, photo
Domestic capacity bands5 A, 15 A, 30 A, 60 A single-phase (230 V); three-phase 400/230 V for larger loads
NEA installation commitmentSingle-phase within 7 days; three-phase within 15 days; TOU meters within about 30 days (announced 2075 BS / 2019 AD)
Lifeline tariff5 A households using up to 20 units/month pay no energy charge, only Rs 30 minimum (ERC tariff effective Mangsir 2078 / Nov 2021)
First wiring inspectionFree of charge; meter, cut-out and service line supplied by and remain property of NEA
NEA customersAbout 5.71 million in FY 2081/82 BS (2024/25 AD), up 4.6 percent year on year
Complaint hotline1150 (NEA central complaint management)
In depth

Who provides new electricity connections in Nepal

Household electricity connections in Nepal are provided almost entirely by the Nepal Electricity Authority (NEA), the state-owned utility created on Bhadra 1, 2042 BS (16 August 1985 AD) under the Nepal Electricity Authority Act, 2041. New-meter applications are handled by NEA's local distribution centres (bitaran kendra), which receive the paperwork, inspect house wiring and install meters. According to NEA's distribution directorate yearbook for fiscal year 2081/82 BS (2024/25 AD), the utility served about 5.71 million customers, up 4.6 percent in a year.

The NEA new connection process is document-heavy but straightforward: it combines proof of identity, proof of right over the property, evidence that the building is legal, and a technical check that the internal wiring is safe before supply is energised. One rule shapes the whole procedure: NEA registers the supply in the name of the legal owner of the premises, payment responsibility stays with the owner, and tenants acquire no ownership rights over the connection. A tenant can still get power arranged for a rented house, but the application normally rests on the owner's documents or a rental agreement plus the owner's consent, so renters should involve the landlord from the start.

Documents required for a new electricity meter application in Nepal

NEA's new customer application form lists a standard set of supporting documents; applicants photocopy each one and present the originals for verification at the distribution centre. Requirements can vary slightly by office — some ask for the latest land-revenue (malpot/tiro) receipt or an extra ward letter when the land certificate is in another family member's name — so it is worth phoning the local distribution centre before queuing.

For rented premises, NEA's guidance accepts a rental agreement as evidence of occupancy, but the connection is still recorded against the property and its legal owner. Where the land has not yet been transferred — for example, a house built by a deceased parent — offices typically ask for a relationship certificate or ward recommendation confirming the applicant's claim before accepting the file.

  • Completed NEA new customer application form (available free at any distribution centre or downloadable from nea.org.np)
  • Copy of Nepali citizenship certificate of the applicant (passport or other ID for non-citizens, per office practice)
  • Copy of the land ownership certificate — lalpurja — for the premises, or a rental/lease agreement for tenants
  • Building construction approval or approved house map (naksha pass) from the municipality, where applicable
  • Ward office recommendation (sifaris), commonly required when documents are not in the applicant's own name or the address needs verification
  • Recent passport-size photograph(s) of the applicant
  • Completed internal house wiring, ready for inspection, done by a qualified electrician

Choosing the ampere band: 5, 15, 30 or 60 amperes — and why it matters

On the application form you must state the capacity you want. Domestic single-phase (230 V) supply is offered in ampere bands — 5 A, 15 A, 30 A and 60 A — while larger houses and non-domestic users take three-phase (400/230 V) supply. The band determines how much load you can draw at once and the monthly service charge you pay, so size realistically: a small dwelling with lights, a television and a refrigerator is fine on 5 A; a family house with a water pump, iron and rice cooker usually takes 15 A or 30 A; homes with electric water heating, induction stoves, air-conditioning or EV charging should consider 30 A, 60 A or three-phase.

Capacity also interacts with the tariff. Under the tariff approved by the Electricity Regulatory Commission (ERC) effective from Mangsir 2078 BS (mid-November 2021 AD), domestic customers with a 5-ampere meter who use 20 units (kWh) or fewer in a month pay no energy charge at all — only a minimum service charge of Rs 30. Higher consumption is billed in slabs (up to 20, 21–30, 31–50, 51–100, 101–250 and above 250 units), with the service charge rising with both the ampere band and the slab; as of October 2022 about 1.7 million households were receiving free energy under the 20-unit provision.

Do not over-buy capacity: you can upgrade later, and NEA has been upgrading 5 A meters to 15 A free of charge in many areas to encourage consumption. Conversely, requesting a band far above your wiring's capacity can complicate the inspection, since the inspector checks that conductors, earthing and the main breaker match the requested load.

NEA new connection process: step-by-step

The procedure below reflects NEA's published guidance for a standard household (single-phase) connection where the distribution line already passes near the property. In 2075 BS (early 2019 AD) NEA publicly committed, through service-charter boards at every distribution centre, to install single-phase meters within seven days, three-phase meters within fifteen days and time-of-use (TOU) meters within about a month of a completed application.

Where the nearest pole or transformer is far from the house or overloaded, the connection becomes an 'estimate' case: NEA surveys the site, prepares a cost estimate for extending the service line, and connects after the applicant deposits that amount. This is the most common cause of delay for houses on the edge of settlements, so check the distance to the nearest NEA line before building.

  • Step 1 — Finish internal wiring with a qualified electrician, including proper earthing and a main breaker (MCB); keep the wiring layout or house map handy.
  • Step 2 — Collect documents: citizenship copy, lalpurja or rental agreement, building approval, ward recommendation and photo.
  • Step 3 — Get and fill the application form at your nearest NEA distribution centre or from nea.org.np; three-phase applicants can apply online at crm.nea.org.np/new-connection.
  • Step 4 — Submit the file, pay the application/service charges and the refundable security deposit per NEA's schedule, and keep the receipt.
  • Step 5 — Wiring inspection: NEA staff inspect the internal wiring and service-line route; the first inspection is free.
  • Step 6 — Meter installation: once the inspection passes and any service-line estimate is paid, NEA installs the service wire, cut-out and meter and switches on supply.
  • Step 7 — Registration: you receive a customer (consumer) number used for all future bills, complaints (hotline 1150) and online bill viewing.

Charges, deposits and service-line costs

NEA's official guidance states that a new customer 'must pay the service charge based on the estimated cost of the connection', which in practice bundles a modest application fee, the connection charge for the ampere band requested, and the cost of any service cable beyond the standard allowance. The meter itself is provided by the Authority — you do not buy your own meter — and the Electricity Rules, 2050 BS (1993 AD) authorise the utility to collect a security deposit (dharauti) against the metering equipment, refundable if supply is never connected or the connection is terminated.

Exact rupee amounts differ by ampere band, phase and distance from the line, and NEA revises its fee schedule periodically, so confirm the current schedule at your distribution centre before paying and insist on official receipts. As a guide, a simple single-phase connection next to an existing line costs a few thousand rupees in fees and deposit, while connections needing new poles, longer service cable or a transformer upgrade are charged per a written NEA estimate deposited in advance. The monthly service charge you will pay indefinitely — from Rs 30 for a low-consumption 5 A customer upward — also depends on the band you choose, and never pay unofficial 'facilitation' money: every legitimate charge appears on a printed receipt.

Wiring inspection, safety rules and your obligations

Before energising a new connection, NEA personnel inspect the premises to confirm the internal wiring meets safety standards — adequate conductor sizing, sound insulation, proper earthing and a functioning main breaker. The first inspection carries no fee. NEA's conditions of supply also warn that if a customer refuses or fails to allow inspection after three consecutive attempts, the Authority may disconnect the supply — a rule that continues to apply after connection, since NEA retains the right to inspect metering and wiring at any time.

The service line, cut-out and meter remain NEA property even though they sit on your building. The customer must protect this equipment; if the meter or service cable is damaged or tampered with, replacement costs fall on the property owner, and meter tampering or bypassing is treated as electricity theft under Nepali law. Keep the meter box accessible for readings, use a qualified electrician, match cable sizes to the ampere band you are requesting, and install proper earthing — a tidy, compliant installation routinely passes on the first visit, which is what keeps you inside NEA's seven-day commitment.

Three-phase, commercial and EV-charging connections: how they differ

Three-phase (400/230 V) connections serve larger homes, workshops, water pumps, lifts and any premises whose load exceeds a 60 A single-phase supply. The paperwork is the same, with two practical differences: NEA runs a dedicated online portal for three-phase meters at crm.nea.org.np/new-connection, and its service commitment allows up to fifteen days for installation instead of seven. Costs are higher across the board — a bigger deposit, heavier service cable and higher monthly minimums — and NEA may check load estimates and transformer capacity before approving, so three phase connection cost in Nepal is always quoted case-by-case through an official estimate.

Commercial and industrial customers are billed on separate non-domestic tariffs that add demand charges per kVA to the energy charge, and high-demand industries connect at 11 kV or 33 kV under agreement with NEA rather than through the household process. A shop operating from a residence should be candid about usage, as supply taken on a domestic tariff but used commercially can be reclassified or penalised. Separately, the Electricity Distribution Bye-laws, 2078 BS (brought into force in 2078–79 BS / 2022 AD) allow households to install a dedicated second meter for charging electric vehicles at home, keeping EV load off the household meter and out of the more expensive upper slabs.

After the meter is installed: billing, name transfer and upgrades

Once connected, you are billed monthly against your customer number: meter readers record consumption, and bills can be checked and paid at NEA counters, through banks and wallets, or via NEA's online customer portal. Pay within the discount window where offered and never let arrears accumulate — reconnection after disconnection for non-payment involves extra charges and paperwork.

When property changes hands, the connection does not transfer automatically: the buyer applies for namsari (meter name transfer) at the distribution centre with the sale deed, new lalpurja, citizenship and the last paid bill, after clearing any dues. Upgrading capacity — say 15 A to 30 A, or single-phase to three-phase — is likewise a fresh application against the existing customer number, with incremental deposit, charges and a new wiring check where needed. Keep every receipt and the meter installation document with your land papers; the paper trail remains the fastest proof of your rights in disputes over billing, deposits or ownership, and it is the file the office will ask for when you later apply for an upgrade, an EV meter or a transfer.

Questions

New Electricity Connection in Nepal: NEA Meter Application Guide — FAQ

How do I apply for a new electricity connection in Nepal?+

Complete your house wiring, then submit NEA's new customer application form at your nearest distribution centre with copies of your citizenship certificate, land ownership certificate (lalpurja) or rental agreement, building approval and a ward recommendation, plus a photo. Pay the service charge and refundable deposit, pass the wiring inspection, and NEA installs the meter — its stated commitment is within seven days for single-phase connections.

Naya bijuli meter kasari banaune — what documents do I need?+

The standard file is: the filled NEA application form, citizenship copy, lalpurja (or rental agreement for tenants), building construction approval or approved house map, a ward office recommendation and a passport-size photo. Some offices also ask for the latest land-tax receipt, and the internal wiring must already be complete before you apply.

How much does a new NEA electricity meter cost?+

There is no single national price: you pay an application/service charge based on the estimated cost of your connection, plus a refundable security deposit that varies by ampere band and phase, while the meter itself is supplied by NEA. A simple single-phase connection near an existing line costs a few thousand rupees in total, but houses far from the network must also deposit NEA's written estimate for extending the service line, so confirm current rates at your distribution centre.

Can a tenant get an electricity meter in a rented house?+

NEA provides supply in the name of the legal owner of the premises, so the connection is registered against the property, and tenants gain no ownership rights over it. A tenant can still submit an application using a rental agreement as proof of occupancy, but the owner's documents and consent are normally needed, and payment responsibility ultimately lies with the property owner.

How much does a three-phase connection cost in Nepal and how is it different?+

Three-phase (400/230 V) connections carry higher deposits, heavier service-cable costs and higher monthly minimum charges than single-phase, and NEA quotes the total case-by-case through an official estimate after checking your load and the local transformer. You can apply online at crm.nea.org.np/new-connection, and NEA's service commitment allows up to fifteen days for installation, versus seven for single-phase.

How long does the NEA new connection process take?+

Under service commitments NEA announced in 2075 BS (2019 AD), single-phase meters should be installed within seven days of a complete application, three-phase within fifteen days and time-of-use meters within about a month. Delays usually come from incomplete documents, wiring that fails inspection, or 'estimate' cases where poles or service line must be extended to reach the house.